  3. alarm does not always resolve correctly

alarm does not always resolve correctly

Scheduled Pinned Locked Moved Support
2 Posts 2 Posters 1.3k Views
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • T
    T
    Tucson
    wrote on last edited by
    #1

    Hi,

    I'm monitoring the states of Windows VMs with thresholds that trigger events.
    The "OS_MAJOR_PROCESS_NOT_RUNNING" event is triggered with the event key "OS_PROCESS_NOT_RUNNING%i".

    This normally works as intended, but sometimes the alarm doesn't resolve when the node leaves maintenance mode.
    Attached are the event logs in .csv format, as well as some details on the individual events.

    Why didn't the alarm resolve with "maintenance leave" (event 8769121)?
    Both "task running" events still reference "maintenance enter" (event 8766568).
    eventlog.csv

    event_8769122.txt

    event_8769123.txt

    event_8768197.txt

    event_8768198.txt

    1 Reply Last reply
    0
    • A
      A
      Alex Kirhenshtein
      wrote on last edited by
      #2

      Hi,

      This is a bug in the server, not your configuration: https://github.com/netxms/netxms/issues/3682

      Here's what's actually happening: when the node leaves maintenance mode, the server re-generates threshold events for every threshold whose state changed during maintenance. That's where your two "task running" events at 04:00 came from. Those events can be processed while the node is still flagged as in maintenance, and then they get correlated to the "maintenance enter" event, which is why they reference 8766568. By default, EPP rules ignore correlated events, so the rule that should terminate the alarm never sees them. It's a timing race, which is why it only happens sometimes.

      Workaround until it's fixed: enable Accept correlated events on the EPP rule that terminates the alarm on OS_PROCESS_OK. As a side effect, the alarm will also be terminated when the task recovers while the node is still in maintenance, which is probably what you want anyway. If the same rule also creates the alarm, split it into two rules and set the flag only on the terminating one. Otherwise alarms will be created during maintenance too.

      1 Reply Last reply
      0

      Hello! It looks like you're interested in this conversation, but you don't have an account yet.

      Getting fed up of having to scroll through the same posts each visit? When you register for an account, you'll always come back to exactly where you were before, and choose to be notified of new replies (either via email, or push notification). You'll also be able to save bookmarks and upvote posts to show your appreciation to other community members.

      With your input, this post could be even better 💗

      Register Login
      Reply
      • Reply as topic
      Log in to reply
      • Oldest to Newest
      • Newest to Oldest
      • Most Votes


      • Login

      • Don't have an account? Register

      • Login or register to search.
      Powered by NodeBB Contributors
      • First post
        Last post
      0
      • Categories
      • Recent
      • Tags
      • Popular
      • Users
      • Groups